ivsenroute
- Florida
What 2 major issues do you see here?
Take a close look.
			Take a close look.
Solid copper wire under the lug with the aluminum.
Strands of aluminum removed.
Butcher job that somebody should be embarrassed by.
Some of the strands of the grounding conductor have been cut off, two wires under one terminal at the neutral/ground block, bonding.
And no bushing
No bushing required, but the SE sheath should stick in at least a 1/4".
And the enclosure is still not bonded.
Take a close look.
All of your posts have no insight as to what YOU think the NEC violations are.
Are we to do your homework for you?
List what YOU think the violations are.
That ship has already sailed my friend. These are old photos from 2009 that were already properly cited and corrected by the ECs. Since you already have a bullseye on my back I will respond.
When I look at my photos, it helps to remind me of the requirements and of the code sections that apply. I want to share these with others who can also hopefully be reminded and/or learn. As you can tell by the replies, not everyone is a walking encylopedia of code references and we all need to pull the book out.
I learn something new every single day, spend thousands of dollars each year on continuing education and appreciate the posts of others when it requires me to open up one of the code books and find an answer.
It is the only way we are going to elevate this industry into a profession.
As you can tell by the photos, many out there still need some help.