Welcome to the forum.Can I run 277 volt ckts & 120 volt ckts in seperate conduits, but then they terminate in one 12x12 junction box for lighting and power purposes.
Is that legal?? per NEC 2008? I thought as long as the insulations of all wires is 600 volts or less it's ok??
Not in NYC 300.3(C)(1) Exception No.2
Barriers shall be provided to isolate conductors energized from different sources when systems voltage exceeds 250 volts![]()
What's their reasoning?
Roger
He is wrong about them occupying the same box it is legal, if you have two devices fed from the two different systems in the same box they must be separated by a barrier.
Roger
Roger,
Care to explain what you mean by two different systems? 208/120 vs. 277/480?
	Rob, that is what I was refering to.
Roger
If I remember correctly there is a phase arrangement (with the graphic that you've shown) where you could end up with less than 300 volts between the devices and therefore a barrier wouldn't be required.
	You are correct, it would depend on which phases of the high and low sides are present. The wording in the illustration below would seem to be taking this into considertion.
Roger
But just from electrical theory, if the this is comming from a different source, you would not read 381 volts between the 2 systems right?? Like current returning to a different sourch. And no, Im not trying to start 'that' thread again![]()