Greeting all,
I have calculated one feeder and breaker size for a project. The total final ampere is 296 ampere included 1.25 for continues.
I have sized breaker 300 ampere with a feeder which has a ampacity capacity of 315 ampere.
Due to voltage drop to compensate the voltage drop the cable size increased one step which has now a ampere capacity of 400.
Now I have got a comment which says " Since your Cable current capacity is 400 you must increase Breaker size too."
I replied back with reference NEC-2008 artical-240, page-179 with Exhibit 240.7.
In this example everything is clear about cable increase size due to voltage drop.
But still I got this comment back to increase the breaker size.
Would anyone please advise me that is there any other reason for this or I have replied right.