Already in the process,,,,,,,,,,,,,,,but my question didnt concern that.
The panel your adding is a second service .
From what your saying your panel in the house is a sub panel. If so requires 4 wire feeder. House must have main breaker unless you only have 6 breakers. And as such neutrals and ground must be seperate and nuetral bar can not be bonded to panel.
Is this allowed in the 2008 code?
the interlock kit prevents a utility back feed
but the 30amp outlet cant feed the WHOLE house
Isnt that now required?
(the generator must be capable of carrying the load without mechanical load shedding)
Why would you make this harder than it needs to be? :-?
Install an interlock kit on the panel and a 30 amp inlet box and call it a day.