- Lockport, IL
- Semi-Retired Electrical Engineer
Is this a neutral wire? If so, then how about 408.41?
Of course it is. That is my point. A conductor (please note: singular) must be terminated under an individual terminal (please note: also singular). The photo shows one conductor being terminated under two terminals. I call that a violation of 408.41.This is a single conductor under two compression points IMO.
You left out the part; that is not used for another conductor. Ther is no other conductor. The intent of this section IMO is to not have multiple circuit neutrals under one termination point.Of course it is. That is my point. A conductor (please note: singular) must be terminated under an individual terminal (please note: also singular). The photo shows one conductor being terminated under two terminals. I call that a violation of 408.41.
As nearly so as is practicable.When you do parallel do you pull the same length wires? I think not.
Yea, but not by much.Then one leg is pulling more amps than the other.
I don?t understand what you are saying here. :-?I would rather split my wire within 3/8" than explain why my feeders aren't the same length.
And of course this is basically the same as what the installer has done but it is legal. :-?
Why do you thing that is legal? Specifically, are you suggesting that you can take a stranded wire, separate the strands into two groups, and land each group on a separate one of the lugs you are showing? I think not.And of course this is basically the same as what the installer has done but it is legal. :-?
Yea, but I had to pay a $2.00 fee to PayPal, in order to collect! :roll:money sent. did you get it? :grin:
Because the lug is listed for the purpose with some panels. In fact, they use to supply them withe , I think, ITE panels years ago. I never said separating the strands was legal in fact I said the opposite.Why do you thing that is legal? Specifically, are you suggesting that you can take a stranded wire, separate the strands into two groups, and land each group on a separate one of the lugs you are showing? I think not.
I'm not sure I agree that it is basically the same.
It's likely that each finger on this lug has a greater ampacity than 1/2 the strands of the wire. Its even possible that each finger is rated for the full ampacity of the wire that the lug is used to terminate. At any rate, the lug is at least UL listed, so its been tested and proven safe.
Did you make sure you sent $1.38 so PayPal could take their cut and charlie still gets a buck? :roll: