Jim W in Tampa
Senior Member
- Location
- Tampa Florida
Sorry Charlie you now owe them $4Yea, but I had to pay a $2.00 fee to PayPal, in order to collect! :roll:
Sorry Charlie you now owe them $4Yea, but I had to pay a $2.00 fee to PayPal, in order to collect! :roll:
I can't find the code section for this :-?
No arguments there, however, the fact that the wire is essentially the same length means that the current will be virtually equal on the split. If this is so then there would be no need to oversize the fingers.
The fact is the code says no--- I just don't see where there should be an issue in this install. Would I turn it down? Probably just to make a point.
Has anyone mentioned 310.4?
I'll assume you are not talking about the lack of white tape. :grin:
I'm sure there is another article but I would use art. 310.4(A) for paralleled conductors being a minimum of 1/0
I see no problem electrically as long as both terminals are tight. In fact, you probably have a better connection to the bus because you have increased the contact area.why would that be a stretch? It is parallel, IMO. Do I think there should be a problem with this-- probably not but I don't see it as code compliant.
Not an issue of any significant electrical consequence.Most stranded conductors have an odd number of strands. That alone will prevent the current from dividing evenly. Some even have 2-3 different sizes of strands.
Nope...You guys don't seriously think that a detrimental current division is going to occur at that point.
Game. Set. Match.Is this a neutral wire? If so, then how about 408.41?
Of course it is. That is my point. A conductor (please note: singular) must be terminated under an individual terminal (please note: also singular). The photo shows one conductor being terminated under two terminals. I call that a violation of 408.41.
My point exactly. The letter of NEC is one thing. The intent is what we hope to get. I won't split hairs over a literal interpretation. The english language is too ambiguous for me to spend time flogging a dead horse.And of course this is basically the same as what the installer has done but it is legal. :-?
![]()
My point exactly. The letter of NEC is one thing. The intent is what we hope to get. I won't split hairs over a literal interpretation. The english language is too ambiguous for me to spend time flogging a dead horse.
Agreed .I don't think the connector shown violates the NEC. I prefer to think of the connector (I use them all the time) as a UL Listed addition to the neutral bus that provides a "single terminal" for the connection of a larger conductor. The neutral wire is still landing on a single terminal. It's all in how you look at it. Is the fitting an extension of the conductor or a mod to the neutral bus? I think its a mod.
Mark
I don't think the connector shown violates the NEC. I prefer to think of the connector (I use them all the time) as a UL Listed addition to the neutral bus that provides a "single terminal" for the connection of a larger conductor. The neutral wire is still landing on a single terminal. It's all in how you look at it. Is the fitting an extension of the conductor or a mod to the neutral bus? I think its a mod.
Mark
When you do parallel do you pull the same length wires? I think not. Then one leg is pulling more amps than the
other; I would rather split my wire within 3/8" than explain why my feeders aren't the same length.
I can't find the code section for this :-?
Insignificant digits....well it could be calculated for extra ohms of the slightly longer wire.
Actually there is white tape, just out of the photo.
Neither are conductors.Also, this would violate Listings, IMHO, since lugs aren't tested this way.