- Lockport, IL
- Semi-Retired Electrical Engineer
Situation: New penthouse added to existing building. Both are concrete with steel rebar. Structural design for penthouse did not involve connecting new rebar with rebar of existing building. Transformer is installed in penthouse. Presently, the XO is connected to ?local? building steel, and is therefore not in electrical contact with planet Earth.
Solution: Chip away enough concrete, both in penthouse and in electric room on floor below, to gain access to the building steel on each floor. Run a ?wire? between the two.
Questions:
1. Will this work?
2. What do you call that ?wire?? Bonding Jumper? Grounding Electrode Conductor?
3. How do you size that ?wire?? 250.66? 250.122? Other?
My problem with this is that we are not really connecting two electrodes together, so we are not in 250.53(C). The building steel in the existing building is an electrode, but the building steel in the new penthouse is not (at least, not yet). So this plan will essentially cause the building steel in the new penthouse to become part of the grounding electrode system, and will cause the wire from XO to penthouse steel to become a successful connection to a grounding electrode.
Questions:
1. Will this work?