Charlie Bob
- West Tennessee
New customer called.She's saying the dryer is not working. there must be something wrong with plug.
I go thereand i found no voltage at plug.go check the breaker,is off,i turn it on.Go back to plug, now we have 245V L-L, 110V L1-N and 115V L2-N.
I tell the guy to check the Dryer, nothing.
I check for continuity, everything is OK. I pluged the cord, and check the connections at the dryer, 245V L1-L2, and 65V L1-n, 178V L2-N. Loose nuetral or broken neutral in cord. Idisconnect the neutral from the cord at dryer connection.I get 245, 110, and 117V at the cord, when i check at the dryer is showing open neutral though.
I tell the customer everything is normal up to the dryer.She needs to get somebody to work on the dryer and find an open neutral.
I charged him half a service call since they were first time customer.
He calls today telling me that a guy went over to work on it, and that light on the dryer came on the first time and then quit, breaker never tripped.
He took it apart and didn't find anything in it.They went and bought another dryer, and they tried it out at the store and worked.
They get home and didn't worked.
They now called me all worked out, they want me back and the guy even told me that it's got to work this time since they already paid me. Hell of a nerve.
What do you guys think could be the problem with this?