A contractor has a 1600A, 277V/480V, 3 phase , 4 wire service. I am putting a ground fault protection as required. Is ground fault indication (light, alarm, etc.) also required to be provided? If so, when in the code is it listed?

Thx
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
A contractor has a 1600A, 277V/480V, 3 phase , 4 wire service. I am putting a ground fault protection as required. Is ground fault indication (light, alarm, etc.) also required to be provided? If so, when in the code is it listed?

Thx
A separate alarm/indication is not required.
 