phase rotation

Status
Not open for further replies.

Hameedulla-Ekhlas

Senior Member
Location
AFG
Greeting all,
I am reading a topic regarding to phase displacement and it says


Phase rotation is always anti-clockwise. (international adopted convention)


Is the red line true?
 

cadpoint

Senior Member
Location
Durham, NC
I thought they called it the "right hand rule" as the power goes forward it curls like the fingers in your hand. Look Up "right hand rule"
 
Last edited:

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Greeting all,
I am reading a topic regarding to phase displacement and it says


Phase rotation is always anti-clockwise. (international adopted convention)


Is the red line true?
No. It is what it is. I live in Northern California where PG&E, the largest utility, is ACB rotation whereas most of the rest of the US is ABC rotation. Not that it matters though, unless someone has designed a Phase Reversal Relay that assumes the ABC convention (and I have run into them).
 

Smart $

Esteemed Member
Location
Ohio
Greeting all,
I am reading a topic regarding to phase displacement and it says


Phase rotation is always anti-clockwise. (international adopted convention)


Is the red line true?
Its true in the sense that is how it supposed to be, i.e. that's how it is supposed to be generated TTBOMK. But simply flopping any two lines will change rotation on any standard 3? system.

There are times when even under code the rotation is changed. For instance, when POCO furnishes a 4-wire delta supply (aka hi-leg service) they may place the hi-leg on line C because that is where it has be for their meter to work properly. However, the NEC requires premises wiring to put the hi-leg on line B... so POCO C is flopped to premises B, thus changing rotation to clockwise. Unless of course POCO takes this into consideration and pre-flops C so the premises flop puts rotation back to "counter-clockwise". In wiring services, the only way to know for sure is to check with a phase rotation indicator.
 

cadpoint

Senior Member
Location
Durham, NC
Talking out of context to the link:
I don't know, I didn't like the magnetic reference to north cause that's really the oppose pole (pointing), that's showing direction to north; nor the inference to a propellar Here because that an object set in motion to do work! The propellar like spinning tires is an eye illusion.
 
Last edited:

shepelec

Senior Member
Location
Palmer, MA
The POCO in my area always sets a clock wise rotation. In turn I ways keep the same rotation through the whole install. I also mark it on the cover of the panels and disconnects. This in turn allows the same rotation to be passed on to any motors as well. It makes start up alot easier if you know what direction evrything is going to turn.:)
 

rattus

Senior Member
Perhaps:

Perhaps:

Greeting all,
I am reading a topic regarding to phase displacement and it says


Phase rotation is always anti-clockwise. (international adopted convention)


Is the red line true?

Perhaps they mean that the arrows representing rotating phasors rotate in a CCW direction. For example, for the phase sequence abc, we would let the instantaneous voltages be,

va = 339V*cos(wt)
vb = 339V*cos(wt -120)
vc = 339V*cos(wt -240)

Then for the phase sequence acb, we could write

va = 339V*cos(wt)
vc = 339V*cos(wt -120)
vb= 339V*cos(wt -240)

In either case the arrows rotate CCW.
 

Smart $

Esteemed Member
Location
Ohio
Perhaps,

Is the abc not clockwise?
When the sequence is noted, it should always be counter-clockwise:
ABC is CCW
ACB is CCW​
If the two were intended to be say alternate systems (such as double-ended supply from two different POCO's), you would not match B's and C's. Rather you would pair A-A, B-C, and C-B respectively on the connection to the gear.

Now if you happen to be talking about phasors, they are static when drawn and yes, their angular position to one another is clockwise (they stay put, you or rather your perspective moves), but the direction which the phasors rotate is counter-clockwise (they move, you stay put)... btw, don't wait for it to happen on paper :D
 

rattus

Senior Member
Much ado about not much.

Much ado about not much.

The term, "phase rotation" is confusing. "Phase sequence" is much more meaningful, that is for the sequence abc, the peaks of va, vb, and vc occur in the sequence abc. For the sequence acb, the peaks occur in the order acb. No need to worry about the direction of rotation.
 

SG-1

Senior Member
The term, "phase rotation" is confusing. "Phase sequence" is much more meaningful, that is for the sequence abc, the peaks of va, vb, and vc occur in the sequence abc. For the sequence acb, the peaks occur in the order acb. No need to worry about the direction of rotation.

Blackburn also makes a very simular comment.
 

Smart $

Esteemed Member
Location
Ohio
The term, "phase rotation" is confusing. "Phase sequence" is much more meaningful, that is for the sequence abc, the peaks of va, vb, and vc occur in the sequence abc. For the sequence acb, the peaks occur in the order acb. No need to worry about the direction of rotation.
That's fine on paper, but in the installation world, ABC and ACB don't mean much when experience has proven that predicting which way a motor will rotate when energized is a crap shoot ;)
 

mivey

Senior Member
J. Lewis Blackburn says the red line is true.
Actually, he probably said the phasor rotation is CCW. If he used the term "phase rotation" I'm sure he did so in the context of "sequence".

As rattus has stated, phase sequence is the proper term. The term "phase rotation" is used but it is not what we might call "proper english".

Rattus properly covered phasor rotation in his post #10
 

mivey

Senior Member
That's fine on paper, but in the installation world, ABC and ACB don't mean much when experience has proven that predicting which way a motor will rotate when energized is a crap shoot ;)
True enough, and the first questions would be: which one is A, which one is B, and which one is C. You just got to have a rotation meter in the field.
 

rattus

Senior Member
That's what I said:

That's what I said:

"Counterclockwise rotation has been adopted internationally as the positive direction of rotation of revolving time phasors." This convention applies to single phase and polyphase systems.

["Alternating Current Circuits", Tang, 1960]
 

rattus

Senior Member
That's fine on paper, but in the installation world, ABC and ACB don't mean much when experience has proven that predicting which way a motor will rotate when energized is a crap shoot ;)

Whatever terms you use, you have the same problem.
 