I work for an engineering firm in Florida. Im designing a RV park, approximately 120 Sites total over (3) buildings.
The NEC has specific requirements for these parks per Article 551 (Revised in NEC 2008). Each Site with a 30A receptacle is REQUIRED to be calculated as 3600VA/Site. I am dropping distribution panels evenly spread out for voltage drop purposes, and each distribution panel will have 12 sites, the distribution panels will be 200A each with (2) 125A breakers feeding a group of 6 sites, (2) breakers total.
I found a charging station for RV''s made by Midwestern electric, and are capable of being loop fed. My REAL question is for this entire post, is for each group (6 sites) if I am loop feeding with a 125A breaker, I know I need to use (2) #1 (1) #6eg, but do I need to carry that through out the entire loop system? That wouldnt make sense because at my last site I would be feeding a 30A site with #1's when I only need #10's.
(OR)
Should I Start at the beginning of the loop with #1's and decrease the wire size as I move past each site (subtracting 3600 watts) ea time.
PS> The voltage here is 240V-1 phase
PSS> Wire sizes above are assuming less then 3% VD.
PSSS> Any other suggestions on designing this would be greatly appreciated.!
(OR)