334.40 Boxes and Fittings.(B) Devices of Insulating Material. Switch, outlet, and tap devices of insulating material shall be permitted to be used without boxes in exposed cable wiring and for rewiring in existing buildings where the cable is concealed and fished. Openings in such devices shall form a close fit around the outer covering of the cable, and the device shall fully enclose the part of the cable from which any part of the covering has been removed. Where connections to conductors are by binding-screw terminals, there shall be available as many terminals as conductors.
I still don't see the Tyco thingies as being legal. According to Dennis's link to 334.80, the cable must be fished. If you're fishing a new cable, why do you need a splice in it?
but, in case Dennis is not your inspector, you might review comments in this thread before using it:
http://forums.mikeholt.com/showthread.php?t=122560&highlight=tyco
So where do you stand on this issue now? BTW, I would never use them. I have replaced a few under trailers that have gone bad and I rarely work on trailers.
Did they fail because of their exposure to the elements? I realize they're not out in the open, but under a trailer or mobile home it can get quite humid.
So where do you stand on this issue now? BTW, I would never use them. I have replaced a few under trailers that have gone bad and I rarely work on trailers.
I have never seen one is use, but my FIRST thoughts come from your link to their product description which seems to indicate it is approved for concealed work in Art 550 & 551 applications and exposed in other applications.
Sorta like if you live in a powder keg, what's one more stick of dynamite going to matter? :grin:maybe becaues its no worse than some other mobile home products
(like the "no box" receptacles)
Did they fail because of their exposure to the elements? I realize they're not out in the open, but under a trailer or mobile home it can get quite humid.
Which wiring method are you refering to; knob-and-tube, NM, MC, etc.can you splice a branch circuit under sheet rock in junction box if you solder it?
314.29 in 05 code. wiring in boxes shall be accessiblein a existing dwelling a homeowner wants a wall removed. The wall has a switch that controls a light on the ceiling he wants the switch moved to a new location the wiring is bx can a handy box with connectors and a blank cover get buried in the wall and solder the conductors where in the nec does it say you cant do this