if you look at 3.2 Applications on the spec sheet for the amp/tyco product, it says its listed for use in manufactured buildings, mobile homes, etc. I dont see anything saying its for use in site built construction.
That is not what it says.These devices can only be "factory installed", according to Section 3.4 of the manufacturer's instructions. They are not to be installed in the field. Sorry. :roll:
Any similar products that serve the same purpose, to be allowed by the NEC, must remain accessible by removal of an old-worked box or be exposed.
It complies with NEC 334.40(B)if you look at 3.2 Applications on the spec sheet for the amp/tyco product, it says its listed for use in manufactured buildings, mobile homes, etc. I dont see anything saying its for use in site built construction.
That is not what it says.
Suprised no one asked the wiring method for the OP - if it were K&T - it very well could be a soldered connection and plastered over.... But not allowed for any other wiring method.
in a existing dwelling a homeowner wants a wall removed. The wall has a switch that controls a light on the ceiling he wants the switch moved to a new location the wiring is bx can a handy box with connectors and a blank cover get buried in the wall and solder the conductors where in the nec does it say you cant do this
Ahhh missed the mention of BX... Saw 'existing dwelling' which could mean anything....Neither solder or those NM interconnectors will work for OP.
Both.What isn't? Tyco 3.4 or NEC 334.40(B)?
334.40(B) Devices of Insulating Material. Switch, outlet, and tap devices of insulating material shall be permitted to be used without boxes in exposed cable wiring and for rewiring in existing buildings where the cable is concealed and fished. Openings in such devices shall form a close fit around the outer covering of the cable, and the device shall fully enclose the part of the cable from which any part of the covering has been removed. Where connections to conductors are by binding-screw terminals, there shall be available as many terminals as conductors.
...
Accessible (as applied to wiring methods). Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building.
...
Concealed. Rendered inaccessible by the structure or finish of the building. Wires in concealed raceways are considered concealed, even though they may become accessible by withdrawing them.
Permitted Uses:
? Where Type NM cable is permitted, and:
?Exposed cable wiring in new work and re-work applications.
?Re-wiring in existing buildings where cable is concealed and finished.
?Installation and interconnection of modular components of manufactured buildings and homes, mobile homes, and recreational vehicles.
NOT Permitted Uses:
? Where Type NM cable is not permitted, and:
?New work where cable is concealed and finished.
Recommended Applications:
?Residential and Light Commercial:
? Add an attic fan or duplex receptacle to an existing circuit.
? Add a ceiling fan to an existing circuit.
? Relocate an existing circuit around a new doorway or new window.
? NEC approved for concealed or accessible applications per NEC Article 334.40(B).
?Modular or Manufactured Buildings, per NEC Article 545.
?Modular, Manufactured, or Mobile Homes, per NEC Article 550.
?Recreational Vehicles, per NEC Article 551.
?Pre-wiring of pre-fabricated walls, per NEC Article 545 or 550.
switch or outlet use with no boxes? I do not find this very clear. Someone please explain this.