Afci's
vsparks
New member
Regarding protection offered by AFCI's I was confused by a statements found on your website and in your book, "Understanding The National Electrical Code" -2002.
Website Q/A: What type of arcs are the most common factors in electrical fires, and will today?s AFCI circuit breakers detect these faults?
An AFCI is designed to detect and clear a line-to-neutral fault under conditions where a standard circuit breaker might not (3 to 8 cycles as compared to 600 half-cycles, depending on the available fault at the failure). Loose electrical terminations and connections should generate enough heat to create a line-to-neutral fault or a line-to-ground fault, which will be detected by the AFCI or GFI circuitry.
2002 Textbook, P.61: "WARNING: AFCI protection devices are not designed to prevent fires caused by series arcing at loose connections to a receptacle, switch, device or in a splice".
Are these two statements contradictory?
Thanks,
vsparks
There are two kinds of arc faults that are now, in the 2008 NEC, required to protect circuits in most of a dwelling unit. These are series and parallel arc faults and I would guess that the series arc fault would be the more common.
Here is an article by Mike Holt that may explain things better for you.
Also an AFCI still may not prevent a fire. Once it has arced, and it has been detected, the breaker should trip, but the conditions for a fire may have already been set.
". . . on your website and in your book . . ."
Welcome to the Forum.
Your inquiry implies that you are addressing Mike H. You are rather unlikely to get a response from him through the Forum.
However, as Dennis & John have already demonstrated, there is a great resource of knowledge and experience in the members of this Forum.
Your observation about the AFCI behavior claims, and the caveat about series arcs, was a source of some frustration with the Grand Concept of the AFCI as sold to us by the manufacturers and special interest groups.
Mike also recommends: Earl Robert's Overcurrents and Undercurrents, All about GFCI's, AFCI's and Similar Devices
Dennis,
Re: "4 Out Of 3 People Have Trouble With Fractions"
The other 50% have trouble with percentages.