Very true, but most folks (make that - most electricians) dont like seeing panelboards and cabling significantly underrun. If you've got full size neutrals, you can't have 80% loading with continuous non-linear loads and expect your panelboard and wiring to survive, as awith (say) 100A 'board with 80A fairly well balanced phase current loads, the neutral probably has in excess of 110A on it, and, sooner or later, theres going to be trouble.Design a robust distribution system and you should not need to take 'special' measures to counter harmonic currents.
Run your 200A panel at 120A max load and you'll probably be fine.
And at the end of the day (or more accuratly, at the end of the wire) the transformer feeding the non-linear loads has to be able to live with the extra temperature rise. K rated transformers are the right answer, but using an oversized standard transformer is a technique with long history...