thats just wrongYes, but this should work:
OMG! Truely pitiful. Make them fix that black bonding jumper while you are at it.
I agree with the "pitiful", but can you give me a Code reference on the black grounding electrode violation.
no argument from me, but grounding electrode conductors ??????Give me a few minutes, I have to go get my code book. I thought there was something about grounded and grounding conductors with insulation that were#6 or smaller not being phase taped.
Bonding jumpers are sized to 250.66 not 250.122. T. 250. 122 is for EGC. The black wire looks like a bond for the steel mesh that is there. I know a GEC does not need to be taped green but am not sure about a bond wire. I believe it is okay as is.Okay Augie, teach this young pup. What am I doing wrong. I do not understand how that wire is a GEC. I would have thought that it was a EBJ and sized by T250.122 according to 250.102(D)
Maybe the location of this would shed some light on the situation. Mexico, perhaps? The Carribbean? Some other remote island that only follows the NEC in principle? This can't possibly be mainland USA. Or could it???? :-?
The rope-a-dope method [cringe]allowed[/cringe] by the NEC for romex is not allowed anywhere (thankfully) else in the code. I have trouble understanding why it is even allowed with romex since it would not be secured to the conduit appropriately, or withing the enclosure. It therefore contradicts other code sections as a concession to the hack.... JMSOI wonder if you ran the wires into a pvc sleeve with a connector (like a 2"1/2)or 2 of them
if it would be code compliant. Like you can do with romex on a surface mount.
Or are you required to use a connector for each piece of mc? Not going to mention the bonding method![]()
How about whiles the MC may be listed for CT use, the conductors may not be, because "no one really knows what type of conductor is inside the cable jacket" as postulated on many other threads on this forum.
EMT connector is not listed for use with MC.
So what happened, someone stripped all of the HR's too short thinking there was going to be a trough?
r.392.3(B) In Industrial Establishments. The wiring methods in Table 392.3(A) shall be permitted to be used in any industrial establishment under the conditions described in their respective articles. In industrial establishments only, where conditions of maintenance and supervision ensure that only qualified persons service the installed cable tray system, any of the cables in 392.3(B)(1) and (B)(2) shall be permitted to be installed in ladder, ventilated trough, solid bottom, or ventilated channel cable trays.
(1) Single Conductors. Single-conductor cables shall be permitted to be installed in accordance with (B)(1)(a) through (B)(1)(c).
(a) Single-conductor cable shall be 1/0 AWG or larger and shall be of a type listed and marked on the surface for use in cable trays. Where 1/0 AWG through 4/0 AWG single-conductor cables are installed in ladder cable tray, the maximum allowable rung spacing for the ladder cable tray shall be 225 mm (9 in.).
(b) Welding cables shall comply with the provisions of Article 630, Part IV.
(c) Single conductors used as equipment grounding conductors shall be insulated, covered, or bare, and they shall be 4 AWG or large