I have a location with a 200a outside 4 space disconnect. 2 of the spaces are for a 100a breaker that services the inside panel. The load calculation for the small apartment is right on 100 a . The 100a breaker trips ocasionally. The apartment is total electric. I am wondering what is is best thing to remove from the inside panel and connect to the 2 other spaces on the outside disconnect ? The dryer, 5 kw heat , 1.5 ton heat pump, water heater , all pull aprox the same av 18 amp . the range would pull more depending on how many burners were on . Even though the range might pull more, I am thinking the heat pump might be best to move since If breaker is on the verge of tripping the starting load for compressor might be more likely to cause a trip. Any ideas ?