wire size

Status
Not open for further replies.

rayman506

Member
when calculating wire size for an resisdential air compressor for a air condition do you go by the minimun ampacity or min/max overcurrent on the label?
 

iwire

Moderator
Staff member
Location
Massachusetts
The NEC allows us to size the conductors by the MCA and at the same time size the over-current protection at the maximum over-current protection rating.

The motors overloads protect the conductors from overload.
 