p51
- south Florida
What would be more efficient ,30 gal. 3500 watt tank type eiectric water heater or a 19kw electric tankless W/H, with the same water usage. Typical 2000 sq. ft. house, 3 bed room ,2 bath.
I think you will find that the efficiency of a tankless design is a little higher but its not as much as the hype would suggest. For less than $100 you can buy a water heater blanket and a timer to shut off the water heater while you are not there (like a setback thermostat) and this system will approach the efficiency of a tankless design at a much reduced cost.
The biggest advantage of a tankless design is you just will not run out of hot water, even if you decide to take a 3 hour shower.
As another poster said, get the gas fired unit if you decide to go this way. Very few homes have a service large enough to use an electric tankless unit and the cost of increasing the service might exceed the cost of the water heater.
I agree with the rest of your post, but there's absolutely nothing that can be done past the point of separation that can be done to compensate for a load-caused voltage-drop ahead of that point.I have also had one where the tankless water heater customer had to pay for a neighbors service upgrade due to voltage drop and flicker issues – they were served out of the same underground pedestal.
Added: In fact, enlarging a heavy user's supply conductors will actually increase the effects their large loads cause to others who share the same transformer or conductors.
The service upgrade didn't help. Only a larger feeder between the utility transformer and the pedestal can reduce the effects of voltage drop one customer's load causes on the other customers.
I went with the gas water heater because of not enough capacity for the electric (the ones that I looked at required a 200 amp feed).
It would cost the same amount of money to run a tankless for one hour as it would to
constantly heat a tank type for 5.4 hours.
Exactly. And the life cost of the tank-less could very well outweigh the minimal loss from the idle tank. When you throw in the cost savings you can get from using a heat pump tank system, it is almost a no-brainer to not use the tank-less if you live in a warmer climate. Also, the HP has a bonus: you get some free A/C in the garage.The only difference in efficiency is whatever energy is lost from the heated water in a tank style unit while it is not in use. And that can be minimized in very cost effective ways.