Is there somewhere in the code that requires an 8/3 or 6/3 NM cable to enter a box with an approved fitting? Or can these wires enter a plastic box when secured with 12 " of entrance to box ?
Deep 4-11/16 metal box with appropriate depth 2 gang ring, and grounding pigtail. Anything else is more problems than its worth in my book. If it's a range, I usually install the ring sideways now instead of facing up and down, cause it makes for plugging in a 4 wire pigtail for a range a whole lot easier.
Can you describe to me what you mean? Are you talking about the conductors going into the device or the cord coming from the appliance?
I used to work for an electrician who always left the 8/3 long enough to stick out of the wall a few feet at the bottom of the floor. Then attach a surface mount range receptacle to the end of the romex and it's easy to plug it in under the range drawer.
Some 2 gang boxes have an opening big enough for an 8/3 romex - so just wondered
That's the guy!If I were to install a plastic box for a range today, I would use the box Larry suggested. It has a extra clamp made for a range cable.
![]()
Yeah, but then you have to bend that #10 EGC around a grounding screw in the box.
That sounds too much like work. :roll:
I just use the green #12 pigtails sold by the bag at wholesale houses and barrel crimp to the incoming EG conductor. "Macmike posts, then ducks and runs from sound of incoming missile fire...."