Old building appears to be about 35 yrs old with 12 office units , electrical room at the end of the complex.
In the beginning it looks like what they had was a 600 amp 3 phase MDP with 60 amp 3 phase service to each unit , MDP fed from ct cabnit.
now here is what is there now.
6 meters that feed 6 - 200 amp 3 phase MLO panels each MLO panel has a 70 amp 3 pole breaker that feeds the unit - this old MDP is now a junction/connection box and what they did is run the feeders from the OLD MDP to each MLO panel to the 70 amp 3 pole breaker then split bolt every thing in the old MDP about 24 split bolts and the old busing was left in place and NO main disconnect at each MLO.
a 7th meter that feeds another 200 amp 3 phase MLO panel ( ALSO NO MAIN DISCONNECT } that feeds the other 6 units with 6 - 60 amp 3 pole breakers one for each of those 6 units.
Never seen such a mess and how he got away with it when ever it was done is beyond me.
What he wants to do now is put the other 6 units on there own meters ( my exact words to him were time an material not to exceed $ 75,000.00 then I went on to explain the existing violations and what needed to be done.
If I have to go back there for anything I will take pictures to post , you guys would not believe it.