- Massachusetts
I am running a subpanel off of a mdp. the mdp is 1200 amps 480/277 volts. I'm running a 3- 500's which are good for 380 amps as the ungrounded conductors and (1) 1/0 for the grounding conductor. My grounded conductor(neutral) load is about 100 amps. Whats the minimum size grounded conductor I can run and where would I find it in the NEC?
Joe, Dennis already mentioned it but it looks like it went unnoticed.
You cannot use 3 - 500s copper for a 1200 amp feeder, you must have conductors with a rating of 1200 amps or more. You cannot roll up to the next size above 800 amps.