The piece of LFMC may need a ground in it. I've never understood why GEC's don't get pulled in. Maybe contractors are just big tight-asses now days because of the economy they can't spare the 10$. I can't remember ever not pulling a GEC. On the other hand if you didn't install the conduit and can't access the entire conduit run, how can you ensure that all the couplings are tight?
You can do a load test. Don't villianize contractors for not installing a redundant GEC to a danged unit heater. It's a unit heater, not a dialysis machine...
villanize wouldn't be my choice of words... I think cheap, lazy, and hard-headed come to mind. I know this has been debated up and down on the forum and there is no politcaly correct answer to satisfy everyone opinion. But if I install it, it gets a ground. The way you do it isn't wrong it's just plan-b for me when I'm 100 miles from the parts house and didn't bring enough. BTW have you ever noticed that there isn't an electrician out there who won't give you their opinion?
we need the picture from the other topic that has the guy getting shocked by the light pole without a GEC
we need the picture from the other topic that has the guy getting shocked by the light pole without a GEC
Wouldn't it be a GEC for connecting grounded conductors on a detached building? EGC definately for branch circuits. Thanks
Metallic conduit is an Equipment Grounding Conductor and is sufficient. (note EGC)
Per commentary in NFPA 99, metallic conduit is noted as being the superior EGC as compared to the insulated conductor, see 517.13(A)&(B)
Roger