K2X
- Colorado Springs
Is it legal to weld on to the ufer
I know from my gc days that most grades of rebar are not suitable for welding, at least not from a structural standpoint.
It was inspected before it was poured by the city inspector. During the pour the vertical portion must have dropped leaving only 2" above the concrete. An alert concrete contractor would have caught this an pulled it up before it dired. Let me see if I can scan a sketch so everyone will get a better picture of what I am talking about.
I was speaking with a gentleman who is on CMP 5. He says that in the 2011 code the wording has changed and the rebar that is stubbed up out of the footer will be considered the Grounding Electrode CONDUCTOR. The grounding Electrode is the 20' in the footer.
This will create another issue, as you will no longer be allowed to use a clamp to attach to this rebar stub up anymore. The stub up being considered the grounding electrode conductor means that you will need to have an irrevsible connection when attaching to it.