II. Requirements for over 600 Volts, Nominal
300.34 Conductor Bending Radius. The conductor shall
not be bent to a radius less than 8 times the overall diameter
for nonshielded conductors or 12 times the overall diameter
for shielded or lead-covered conductors during or after installation.
For multiconductor or multiplexed singleconductor
cables having individually shielded conductors,
the minimum bending radius is 12 times the diameter of the
individually shielded conductors or 7 times the overall diameter,
whichever is greater.