ceb58
- Raeford, NC
Situation boss wants. Revamping an old communication tower and building. The gen set will be installed inside the comm. building but I have a pad to pour out side for the lp gas tank. The tank will be located about 12ft from the building. The gas line I will install is plastic. The risers are metal above ground then transition to plastic with the stab locks for the pipe. When I come into building I will run black pipe to the gen set and connect with a flex hose provided with gen set. Gen. set will be of course bonded with EGC. What boss wants to do is run an EGC to the gas tank, install a lug on one of the legs and tie the EGC back into the halo grounding system for the building. Unsure on this. There will be no metallic connection between the tank and building and if/when the system takes a hit could it cause or be more dangerous to have the EGC on the tank?