He is at it again:
Here is a list of things I failed a FINAL for here in North Jersey:
1. Seal-tite is not sunlight resistant.(Marked right on it S/R)
2. No service receptacle at condensing unit.( 20' away in sight on front of the house is an existing one)
3. Can not use existing waterpipe clamp on street side of water meter.( No rust corrosion and was brass practically new..?????)
4. Need UL Listed breaker lock for free-standing range.(WHY????)
5. Install Gem extenders on all tile areas.(Boxes were flush to tile..no set-back. WHY?????)
6. Install intersystem bonding connection at service for communications.(This was NOT NEW CONSTRUCTION......THIS IS REHAB CODE!!!!!)
This is RIDICULOUS and I will be emailing Suzanne Borek in the morning!!!
Any fellow NJ contractors care to comment??? Other are of course welcome.