Sparky32297
 - right here
OK, I will try and paint a picture
200 amp disconnect on out side of house with 2 ground rods going to it.
Inside there is a 200 amp panel fed with 2 hots a neutral (proper size) and a #4 copper ground wire from service disconnect.
The electrician has run #4 copper ground wire from the water pipe (within 5' of entrance to house) to the sub panel.
One inspector is of the opinion that placing the wire from the water pipe in the ECG bar is sufficient and covers the grounding requirements of the service.(The ground wire from the water pipe can be removed from the ECG bar with a screwdriver)
The other inspector thinks that the wire from the outside service and the wire from the water pipe should be joined with an irreversible connector and then take a tail from this down to the panel. This eliminates the ability to break the continuity to the service in his opinion.
Thoughts?