laketime

Senior Member
I am pricing out a house and the g.c. wants me to plan for a 400amp service. What would you guys use to tie the meter to the panel? Was going to use SER cable for a 200 amp but not sure with 400 amp.
 
Can you use a meter combo 400 amp-- no service work to do except drive the rods and hook up any GEC.

Usually I use a 400 amp base and have two 200 amp panels one on each side of the meter. I use 3/0 copper for the service entrance conductors.
 
I am pricing out a house and the g.c. wants me to plan for a 400amp service. What would you guys use to tie the meter to the panel? Was going to use SER cable for a 200 amp but not sure with 400 amp.




Rob is hiinting you in the right direction.

Under 05' the 42 circuit rule is in effect, so I would use (2) 200's.

Under 08' you could use one big panel if you choose.
 
Never hooked up a 400 amp residential service. So basically get a 400 amp meter and feed two separate 200 amp load centers off the meter?
 
Rob is hiinting you in the right direction.

Under 05' the 42 circuit rule is in effect, so I would use (2) 200's.

Under 08' you could use one big panel if you choose.

Under the 08 two 42 circuit panels are usually more than enough. I don't get where you are going with this. I think rob was getting at the service conductor size.
 
Under the 08 two 42 circuit panels are usually more than enough. I don't get where you are going with this. I think rob was getting at the service conductor size.




We need to KNow if he's feedind one panel or two,,,it's as simple as that. I'm not going anywhere with it.

And 42 are not always enough.I just did a house with a 400 amp base feeding (2) 200 amp service panels, feeding (2) 200 subpanels, (2) 100 subpanels,and (2) 50's throughout the house.


I was simply telling him we need to know how many he is using
 
Well for one big 400 amp panel you could use 310.15(B)(6), for two 200 amp panels you cannot. That's where I was going. :)
 
We need to KNow if he's feedind one panel or two,,,it's as simple as that. I'm not going anywhere with it.

And 42 are not always enough.I just did a house with a 400 amp base feeding (2) 200 amp service panels, feeding (2) 200 subpanels, (2) 100 subpanels,and (2) 50's throughout the house.


I was simply telling him we need to know how many he is using

Not sure yet. GC wants a price for 400 amp service. So it sounds to me the cheapest way to provide that is a 400 amp meter feeding two 200 amp panels?
 
Not sure yet. GC wants a price for 400 amp service. So it sounds to me the cheapest way to provide that is a 400 amp meter feeding two 200 amp panels?
That is my MO-- I usually use two 200 amp feed thru panels outside and then feed inside with two 40 cir. panels
 
OK so i would go from a 400 amp meter to a 400 amp panel with a main breaker, then to two sub 200 amp panels with main breakers?
 
Yeah that is what I was thinking. A 400 amp main, double lug 3/0's to two separate 200 amp load centers with a main breaker.
 