Ok everyone I have a few questions. Here is an example and its setup.
200A Load Center in a Manufactured Home
200A disconnecting means outside on pole(required by utility company)
Ok now correct me if I am wrong. Since the disconnect is outside... the grounded conductor and equipment grounding conductor(s) shall be bonded by a main bonding jumper which in this case could be a #4 AWG Cu wire NEC 250.28(D)(1)----> (Table 250.66) from the ground bar in the inside load center to the neutral bar in the outside disconnect. I guess another option could be to use an EGC sized by 250.122 #6 AWG Cu run it from inside ground bar to outside ground bar then make main bond in outside enclosure either by screw already provided or the previous sized #4 between the ground and neutral bars. The latter would probably save on wire cost. Remove main bonding jumper in inside load center. Then the load center is no longer your service disconnecting means. May depend on AHJ how to do it.
Someone please elaborate the equipment bonding jumper. Is this mainly aimed at electrically connecting any non current carrying equipment such as load centers, conduit, subpanels, metal boxes together via bonding locknuts, wire, etc.?
What is the most economical disconnecting means outside? Safety switches are expensive as load centers. Would like something simple and small but if a big enclosure is cheaper then I guess it's better to go with that. Any suggestions?