jumper
- 3 Hr 2 Min from Winged Horses
alot im kinda new to the trade i might ask again later who knows lol
We are all here to learn.
the question is: Can the grounding conductor be larger than the grounded conductor or vice versa? where does it state this in the nec?
In most cases your neutral is bigger than your ground. What is your app?
Jumper,
I have not seen any NEC artical to recommend neutral conductor size bigger yet but it is possible when we have a nonlinear load and harmonic because overheating of neutral conductors due to third harmonic currents flowing through the neutral. The size of the neutral must be increased by 150-200% of the normal size in such cases, depending upon the severity of the harmonics.