Bob,
Are you evil?
Grounds start getting big when it gets to parallel runs per 250.122(F) -
I agree the requirements in 250.4(A)(5) and (B)(4) are vague and possible unenforceable.
Chris
Well I had to think because the original thought I had was wrong. I was thinking if the egc had to be upsized based on art. 250.122(B), then the grounding conductor would have to be larger than the grounded conductor. I don't think this is correct because the neutral would have to bve at least the same size as the grounding conductor in order to safely clear ground fault.Okay, I will bite. When? I ask only to learn.
:grin:
Who ... me?
how you can say vague there is nothgin vague in NEC. Please read the below for reason.
In NEC-250.4(A)(5), we find a definition of an effective ground fault current path
" An intentionally constructed, permanent, low impedance electrically conductive path designed and intended from the point of a ground fault on a wiring system to the electrical supply source and that facilitates the operation of the overcurrent protection device or ground fault detectors on high impedance grounded system"
Under fault current condition, the possible burning off of an equipment grounding conductor, a bonding jumper, or any conductor that is dependent upon safely carrying fault current until the overcurrent protective device can clear the fault result in a hazard to life, safety and equip,ent.
Well I had to think because the original thought I had was wrong. I was thinking if the egc had to be upsized based on art. 250.122(B), then the grounding conductor would have to be larger than the grounded conductor. I don't think this is correct because the neutral would have to bve at least the same size as the grounding conductor in order to safely clear ground fault.
Specifically I was thinking of a feeder to a panel where the neutral load was minimum (10 amps or so) but the feeders OCPD where a 100 amp.
I now realize that the neutral cannot be smaller than the grounding but could be the same size.
Hameedulla-Ekhlas, thinking we have different sized code books...my Table 250.122 is on page 117. To keep clarity in mind, if we define it by Article and section number, it won't matter what page it is on, we will both be on the same page for gleaning the information.
And am in the boat that the grounded or grounding conductors will not be larger than any of the current carrying conductors that are protected by an ocpd.
Fast enough to "prevent extensive damage to the electrical components of the circuit".Can you point out the NEC section that specifies exactly what an effective ground fault current path is?
Just how fast does the OCPD have to operate?
Just saying .....
Here is what I meant by vague, (And there are many things in the NEC that are vague)
The definition that you posted does not contain any prescriptive measures as to what is considered an "Effective ground fault current path".
What would be considered to be low impedance?
Chris
I dont have any different book with me. It is a NEC-2008 blue cover with three names
Mark W.Early
Jeffrey S.Sargent
Joseph V.Sheehan
E. William Buss
Eleventh Edition
Exactly page-249
Here is what I meant by vague, (And there are many things in the NEC that are vague)
The definition that you posted does not contain any prescriptive measures as to what is considered an "Effective ground fault current path".
What would be considered to be low impedance?
Chris
Well I had to think because the original thought I had was wrong. I was thinking if the egc had to be upsized based on art. 250.122(B), then the grounding conductor would have to be larger than the grounded conductor. I don't think this is correct because the neutral would have to bve at least the same size as the grounding conductor in order to safely clear ground fault.
Specifically I was thinking of a feeder to a panel where the neutral load was minimum (10 amps or so) but the feeders OCPD where a 100 amp.
I now realize that the neutral cannot be smaller than the grounding but could be the same time.
so the questions still stands where in the nec does it say my neutral cant be bigger then my grounding
That has been answered numerous times already. The nec does not say that and in most cases the neutral is larger than the grounding (EGC) conductorso the questions still stands where in the nec does it say my neutral cant be bigger then my grounding
so the questions still stands where in the nec does it say my neutral cant be bigger then my grounding
Almost. The grounding conductor can be larger than the ungrounded conductors but there is no need to do that and a waste of wire.so im safe to say the only rule that would apply would be that my grouding just couldnt be bigger then my conductors 250.122(A)