LarryFine
- Henrico County, VA
- Electrical Contractor
"Here I come to save the daaaaayyyyy!" :grin:Where is Larry, he know's.
Picture a typical 3ph breaker, which would pick up each phase by the stab clips. Now, because your panel only has two buses, the third breaker body has no clip, but just has an empty stab slop.
Now, to get the third phase into the third breaker body, a fourth body is added (which may have a mechanism in it, or may just be a 'jumper') which provides a terminal for the third phase to get in.
A and B phases are obtained as usual, through the MB or ML's and the panel buses and stabs, and the high leg is obtained by being routed from the 3ph meter directly to the fourth breaker body.
So, you see how easy it would be to add a high leg to an existing 1ph service. You'd only have to replace the meter guts and add a wire from the POA to the meter, and meter to Delta breaker.
You could theoretically build a Delta breaker by combining a regular 2p breaker with a 2p breaker with the clips removed and internally jumpered together. You wouldn't have the internal trip, tho.
Added: Good luck finding a 4p handle tie, too.