Customer has a single phase, 120 volt, FPB with a MCA of 20.7 amps, Max OCPD 25 amps. Wants to use a 20 amp snap switch for the disconnect on a 25 amp circuit. Sound good? I said yes.
Customer has a single phase, 120 volt, FPB with a MCA of 20.7 amps, Max OCPD 25 amps. Wants to use a 20 amp snap switch for the disconnect on a 25 amp circuit. Sound good? I said yes.
430.110 seems to back this up.For what reason? My thought was that the disco needs to 115% of the running current not the MCA.
I am confused, how can you say yes without knowing the full load current rating of the motor?For what reason? My thought was that the disco needs to 115% of the running current not the MCA.
I am confused, how can you say yes without knowing the full load current rating of the motor?
I believe you are right. Thanks. Brain is half on tonight. I guess yes would be the appropriate answer. :roll:Doesn't FLC x 1.25= MCA? Left book in truck.
Customer has a single phase, 120 volt, FPB with a MCA of 20.7 amps, Max OCPD 25 amps. Wants to use a 20 amp snap switch for the disconnect on a 25 amp circuit. Sound good? I said yes.
I looked again today and I was mistaken this is actually a VAV box with an electric heating coil. The unit contains no fan.
So that would mean that the switch needs to be rated at 125% of the full load. Also provisions of adding a lock for LOTO.(424.19)