Square Footage: Living: 1940 sq-ft (per measurement of outside dimensions of space), +260 sq-ft of space in crawl space to be closed in for small workshop.
Bathrooms - 3
Laundry - 1
Attic Space - 1
Crawl Space with access - 1
Water Heater: 240V, 5.5kW
Range: 8kW (per Column C of T220.55)
Refrigerator: 11.2A, 120V... I used 12A (80% loading rule) since this item is replaceable. Though on an exam question, the 11.2 A would have to be used.
Dishwasher: 9.0A, 120V
Microwave/Range Hood combo unit: 1kW
Dryer: 240V/26A: 6.24kW
Garage Door Opener: All I could find on the rating was 1/2hp, so per T430.248: 9.8A @ 120V. And per 430.24, 1.25*9.8*120=1470VA
Receptacle Load beyond those Required in Article 210:
1 in garage + 1 run outside to garden + 8 in workshop area
Lighting Load beyond those Required in Article 210:
1 in Kitchen (non-linear rated 204 VA)
6 in crawlspace and workshop area
Additional Fixed Load:
3 bathroom ventilation fans @1.17A each, 120V
1 whirlpool tub whose motor is rated 7A for 120V, 840VA
HVAC:
Unit 1: Package Gas Furnace and A/C: Min Ckt Ampacity: 17.9A @240V
Unit 2: Split Unit Heat Pump:
Outdoor Unit: Min Ckt Ampacity: 14.1A @240V
Indoor Unit: Min Ckt Ampacity: 33.5A @240V for blower + 8kW auxilliary heat.
With the Artical 220 Parts I-III I get 227A, with Part IV (Optional) I get 160A. Though I didn't include the workspace in the sq-ft calc and am wondering if I should've.