The Project Engineer, using a engineered supervised calculation, has determined using 3 sets of 750 kcmil XHHW-2 copper with 1-1/0 copper XHHW-2 ground for a 800 amp 480 volt 3 phase 3 wire branch circuit to a MCC. Mainly due to being in a duct bank with heating issues.
It is my determination that the EGC needs to increased in size to a 250 kcmil, to be in accordance to NEC 250-122(B).
The Engineering firm is objecting stating this is not correct, because they are not increasing the size of the ungrounded conductors, but found the size needed to carry by using the calulations to determine the ampacity as NEC 310.15(A)(1) allow.
I am asking for some input on this.
It is my determination that the EGC needs to increased in size to a 250 kcmil, to be in accordance to NEC 250-122(B).
The Engineering firm is objecting stating this is not correct, because they are not increasing the size of the ungrounded conductors, but found the size needed to carry by using the calulations to determine the ampacity as NEC 310.15(A)(1) allow.
I am asking for some input on this.