Steve, I think that I agree with you.
So in your opinion you would start with the smallest permitted conductors and any larger deviation from those conductors would make 250.122(B) applicable? So in the case of this scenario the EGC could be the same size?
Rob:
The starting point does seem a little vague here. But I think one could reasonably claim that either #8 or #6 is the "starting size conductor" for 50A. So I wouldn't have any problem with someone running a #10 ground with either.
Another issue that I think is somewhat similar: For a 400 amp feeder, I think one could claim that either 500KCM or 600 KCM is the starting size conductor.
In both cases, I would tend to give the "benefit of doubt", and say that the larger size is what you use as your starting point.
This may sound like I'm contridicting my previous point of "use the smallest size allowed", but for example, #8 wouldn't be allowed for a 50A circuit if the terminations are only rated 60 deg.
Steve