troffer whips

Status
Not open for further replies.

stew

Senior Member
Why is it that the manufacturers can install a whip with #16 wire connected to a 20 amp circiuit but if I have a troffer of the same type say a 4 ft 3 lamp unit I cannot use a wire size smaller than 12 for my whip?
 

stew

Senior Member
the reason I wondered is that I installe some troffers the other day that may have actually had 18 in the whip. I wondered about it but then realized that the whip is nothing more than an extension of the wire from the ballast. It the ocurred to me that hey why the heck cant i do the same thing . UL we dont neede no stinkin UL!!! It makes no sense to me at all!!!
 

cadpoint

Senior Member
Location
Durham, NC
I'm not going to defend the UL.

But if you think about for a minute, if you were to consider voltage drop for the application where would you put the smallest wire? Assuming one needed a smaller wire(IE their assembly)?

Yes there skirting the code, but then there's the Code otherwise.
 

benaround

Senior Member
Location
Arizona
stew,

The premise wiring stops at the j-box that the fixture whip ties into. The premise wiring

also stops at the wall recpt. but look at all the small gauge wire on the things we plug in.

Fixture whips are for suppling 'one' fixture, not for branch circuiting many fixtures all

together. And yes, we do need U.L. :)
 

ceb58

Senior Member
Location
Raeford, NC
the reason I wondered is that I installe some troffers the other day that may have actually had 18 in the whip. I wondered about it but then realized that the whip is nothing more than an extension of the wire from the ballast. It the ocurred to me that hey why the heck cant i do the same thing . UL we dont neede no stinkin UL!!! It makes no sense to me at all!!!

I am not saying UL is perfect but can you imagine the crap that would be out there with out it.
The MFG. spend large money to design and prove there product is safe. In this case they have convinced UL that the fixture is safe with 18. Look at what the A/C mfg. do. By the NEC we size our wire and OCP per mfg name plate. Which lets us use smaller wire with larger OCP than we can any where else in the NEC. All because the A/C mfg. have install there own protection and have engineered and proven the operating conditions for there equipment.
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
That whip is just for that 1 fixture. It is plenty safe and it is not the thhn that your using. That does not mean it has not or will not be abuse by adding fixtures and we all have seen that. UL covers them.
 

mcclary's electrical

Senior Member
Location
VA
What about a lamp with 18 guage cord? What about a 16 guage extension cord? They all are not premise wiring. Be careful with fixture whips on layins, many local AHJ's have adopted no whip policy
 

stew

Senior Member
I fully understand what eveyone is saying I just think i does not make any good sense to have to use a # 12 whip to feed a load that is .8 amps.And neither does ul or the manufacturer that why the get approval to use thier weenie whips. But me? Nuh huh. no can do I would surely cause a fire if I used a 14 on these!! HA HA HA . It just seems to me that if the whip isnt over 6 fdt whats the big deal eh?
 
Last edited:

Jim W in Tampa

Senior Member
Location
Tampa Florida
I fully understand what eveyone is saying I just think i does not make any good sense to have to use a # 12 whip to feed a load that is .8 amps.And neither does ul or the manufacturer that why the get approval to use thier weenie whips. But me? Nuh huh. no can do I would surely cause a fire if I used a 14 on these!! HA HA HA . It just seems to me that if the whip isnt over 6 fdt whats the big deal eh?
Big deal is that someone seeing your install might tap in and add more fixtures. I agree if not misused is no danger but same would apply to ceiling fan / light combo and simply is a no can do. Why is number 12 such a big deal ?
 

mcclary's electrical

Senior Member
Location
VA

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
There is no reason why you can't make your own fixture whips using conductors with an ampacity of less than the branch circuit rating. 240.5(B)(2)(1) permits you to use up to 50' of #18 tapped off a 20 amp branch circuit, or up to 100' of #16 tapped off that same 20 amp branch circuit.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Look at what the A/C mfg. do. By the NEC we size our wire and OCP per mfg name plate. Which lets us use smaller wire with larger OCP than we can any where else in the NEC. All because the A/C mfg. have install there own protection and have engineered and proven the operating conditions for there equipment.
There was something in it for them: adequate handling of starting current.

Imagine being told we have to run #6 to a 30a AC because of the required breaker.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
240.5(B)(2)(1) permits you to use up to 50' of #18 tapped off a 20 amp branch circuit, or up to 100' of #16 tapped off that same 20 amp branch circuit.
But, what's the load limit/fixture count on those conductors?

I can't wait for the flood of "Then why can't we use #14 for switched fixture legs on 20a circuits?!" responses.
 

Cavie

Senior Member
Location
SW Florida
How do you daisy chain through a whip? unless you put two in each light

You jump from fixture to fixture using the whips. The fixtures can only be 4' apart. I've seen it done but I wouldn't do it. It's much cheaper in the long run to buy whiped fixtures than non whiped and have to make up the whips. Big labor savings.
 
Last edited:

mcclary's electrical

Senior Member
Location
VA
You jump from fixture to fixture using the whips. The fixtures can only be 4' apart. I've seen it done but I wouldn't do it. It's much cheaper in the long run to buy whiped fixtures than non whiped and have to make up the whips. Big labor savings.



I didn't think anybody was stupid enough to do that. When you buy a whipped fixture, and then add another whip, you should automatically know that's not right.
 