I have a 3 phase 200 amp 3/0 thhn service coming from meter can in EMT to apt 4 floors up is it necessary to run a seperate ground green wire #6 to panel ????
I have a 3 phase 200 amp 3/0 thhn service coming from meter can in EMT to apt 4 floors up is it necessary to run a seperate ground green wire #6 to panel ????
I have a 3 phase 200 amp 3/0 thhn service coming from meter can in EMT to apt 4 floors up is it necessary to run a seperate ground green wire #6 to panel ????
My guess is no since you are using emt. The emt can be used as your ground. Art. 358.60
I know we sometimes get bogged down by semantics, but this is a good example of a situation where using the proper termination makes it very clear. The NEC defines "Service" as "the conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served". Since you are not a utility, you are not running "service" to the apartment. Your question then becomes much simpler: "I am running a feeder from the service disconnect to an apartment on the fourth floor of a building. Can the EMT conduit serve as the grounding conductor for this feeder, or do I need to install a separate grounding conductor?" 250.118 provides a list of acceptable grounding conductors. You will see that EMT is on the list, so it may be used as the grounding conductor for this feeder.
Words are important...