calisparky6
i want to install in 3/4 EMT  3#6 THHN  with 2#10 THHN with a #10 ground.  my calculations show that conduit fill at 40%  code book shows .213 sq/in and my fill comes in at .215.  im not compliant right...and i should install 1".
			i don't see where the code permits us to use the actual dimensions for single conductors. In the Chapter 9 Notes to the Tables, Note 6 requires us to use the dimensions in Tables 5 and 5A for wire fill calculations involving multiple sizes of single conductors.Possibly.
As noted in the NEC tables, size is approximate. Check with manufacturer of wire for nominal size. For example, Southwire's simpull thhn nominal OD sizes are #6 at .249" and #10 at .161. The Chapter 9 tables put these sizes at .254 and .164 respectively. The difference would make your impending installation compliant.
Darn... forgot about that.i don't see where the code permits us to use the actual dimensions for single conductors. In the Chapter 9 Notes to the Tables, Note 6 requires us to use the dimensions in Tables 5 and 5A for wire fill calculations involving multiple sizes of single conductors.
3 - 6 AWG and 3 10 AWGs?
. my experience says that is going to be a tough pull in 3/4".
Derating comes to mind as well.
Chances are good the #10's are OK, but what are you planning to fuse the #6's at??
Are you sure?... i cant run a bare ground because its considered a "feeder" because i'm feeding the spa disconnect gfci. ...
Smart-- what are you saying is news to you. The fact that it's a feeder or that a bare conductor cannot be run.Are you sure?
That's news to me.
If your OCPD is 50A and you're upsizing the ungrounded conductors from #8 to #6 for voltage drop, you must also upsize the EGC from #10 to #8 [250.122(B)]... it calls for #8 but because the run is over 100'...i went with #6. ...
Please cite a code reference so we know what requirements you are discussing. Offhand I know of no rules stating such... but pools and spas are not my forte.also the code is contradictory..in one case it calls for disconnecting means to be no more than 5' and then in another section it calls for disconnecting means to be no less than 5'?
680.41 Emergency Switch for Spas and Hot Tubs.
A clearly labeled emergency shutoff or control switch for the purpose of stopping the motor(s) that provide power to the recirculation system and jet system shall be installed at a point readily accessible to the users and not less than 1.5 m (5 ft) away, adjacent to, and within sight of the spa or hot tub. This requirement shall not apply to single-family dwellings.
I'm not saying a bare EGC cannot be run.... cali' is. I'm the one that suggested running a bare EGC to begin with. If running a bare EGC is not permitted for run in conduit, please cite a reference... especially regarding a feeder for this case.Smart-- what are you saying is news to you. The fact that it's a feeder or that a bare conductor cannot be run.
680.25(B) Grounding. An equipment grounding conductor shall be installed with the feeder conductors between the grounding terminal of the pool equipment panelboard and the grounding terminal of the applicable service equipment or source of a separately derived system. For other than (1) existing feeders covered in 680.25(A), Exception, or (2) feeders to separate buildings that do not utilize an insulated equipment grounding conductor in accordance with 680.25(B)(2), this equipment grounding conductor shall be insulated.
Smart the OP is confusing the disco with the emergency Off switch for other than single family dwellings.