This note relates to a thread from 2003 discussing an overheating of a breaker switch.  That thread never came up with a definitive answer so I am writing with what I found.
I had an overheating breaker problem on an air conditiioner compressor circuit (220 single phase) where a 40 amp breaker would heat up and trip after the unit was running for about 1/2 hour. Measuring the current on the circuit indicated 14 to 15 amps - the breaker is rated at 40 amps. The breaker was too hot to touch when it tripped.
The problem was due to a bad connection in one of the screw terminals. The conductor material is aluminum (Copper would be better) and cleaning up the wire ends and the screw terminals did the trick. I also made sure the screws were really tight. Now the breaker runs cold and it doesn't trip.
Fixed.
Great forum!
Fixed.
Great forum!