How's that?
Seems good to me.
How's that?
If you think I twisted your words than tell me again about how a standard breaker will or will not protect about ground faults without trying to make me or anyone else look stupid.
Well I guess we are even as I have been tired of your condescending attitude with everyone for a long time.
How about a simple explanation: The trip mechanism will trip when it reaches a certain temperature.
Current and externally-supplied heat both contribute to the mechanism reaching that temperature.
The greater the externally-supplied heat, the less current needed to reach the tripping temperature.
Ambient temperatures and heat from poor connections both contribute to externally-supplied heat.
How's that?
... as all metals do, have thermal memory, and will tend to retian thier shapes. This will cause the trip charteristics of a thermal breaker to change following a condition as the OP described. That is why I suggested testing the breaker, or replacing it, before saying everything was fixed.
That is all correct. Now here is the issue and the reason I regrettably posted to this thread. Sustained heating, from something such as a high resistance connection can permantly change the charteristics of the bimetallic strip in the thermal element, the metals, as all metals do, have thermal memory, and will tend to retian thier shapes. This will cause the trip charteristics of a thermal breaker to change following a condition as the OP described. That is why I suggested testing the breaker, or replacing it, before saying everything was fixed.
That is all correct. Now here is the issue and the reason I regrettably posted to this thread. Sustained heating, from something such as a high resistance connection can permantly change the charteristics of the bimetallic strip in the thermal element, the metals, as all metals do, have thermal memory, and will tend to retian thier shapes. This will cause the trip charteristics of a thermal breaker to change following a condition as the OP described. That is why I suggested testing the breaker, or replacing it, before saying everything was fixed.
<snip>
The problem was due to a bad connection in one of the screw terminals. The conductor material is aluminum (Copper would be better) and cleaning up the wire ends and the screw terminals did the trick. I also made sure the screws were really tight. Now the breaker runs cold and it doesn't trip.
Fixed.
Great forum!
I will agree that over time the repeated heating will change/damage the breaker. Personaly I would not have done as the OP as far as cleaning and such for the breaker. A 40 dp is not worth the risk and is not worth the time and expence of haveing it tested. Install a new one, charge for it and be on your way.