1793
Senior Member
- Location
- Louisville, Kentucky
- Occupation
- Inspector
I'm installing a sub-panel fed with a 60A 2p breaker in the main panel.  I will be pullin in 3 #6's and a #10 for the EGC.  I have an issue where I want to move 8 circuits from one panel to the new sub-panel  using a 1" Sch 40 PVC nipple.  The nipple is about 4" in length so I don't have to be worried about the derating of 310.15(B)(2)(a).
 
My question is do I have to reroute the EGC's of the eight circuits or can I leave them in the original, main, panel?
 
As always thanks in advance.
	
		
			
		
		
	
				
			My question is do I have to reroute the EGC's of the eight circuits or can I leave them in the original, main, panel?
As always thanks in advance.
 
				
 
 
		 
 
		 
 
		 
 
		