Question on UFER Ground
KWH
I have a service consisting of two 200amp main breaker panels concerning the ufer ground can I install 1 #4 bare from rebar, terminate wire in one panel then split bolt off this wire to the other panel, when dealing with a ground rod I would have run a seperate wire from each panel to the ground rod terminating under seperate clamps.
Thanks
Thanks
I don't see a question but if you are asking if this is compliant I would say yes.
We always terminate in the meter to avoid terminating in two panels. Some areas won't allow this but fortunately they allow it here.
Ufer Ground
Ufer Ground
Dennis, I was wanting to make sure I could ground both panels with one wire.
Thanks
Thanks
Yes, I thought I answered that. The ufer gfoes to oone panel and you split bolt a #4 of the ufer to the second panel. This is code compliant. Does that answer it or am I still off.
Dennis you covered it thanks to all
I was confusing this with how I alway's did my ground rods.
Thanks
You can tiewire shorter sections of rebar together to achieve the overall 20' length.
Chris
Thanks for the quotes. Had not looked at 264 in a long time.
I am baffled by the idea that
a tie-wire makes a good electrical joint,
in concrete after corrosion and rust set in.
If you landed the UFER in one panel, wouldn't that connect the second panel through the neutral in the meter can??
You would think so but 250.64(D)(1)does not appear to accept that as a method of bonding the enclosures.
Without quoting any text, I don't think that we want to let the grounding of one service disconnect enclosure and Grounded Conductor to be dependant on another backfed that way.
If the first panel is compromised, the second will not be earthed.