I have a service consisting of two 200amp main breaker panels concerning the ufer ground can I install 1 #4 bare from rebar, terminate wire in one panel then split bolt off this wire to the other panel, when dealing with a ground rod I would have run a seperate wire from each panel to the ground rod terminating under seperate clamps.
Thanks