Would a recepticle mounted at 18" aff behind the dishwasher satisfy the accessable part in
422.16(B)(2) and 422.33(A)
422.16(B)(2) and 422.33(A)
Would a recepticle mounted at 18" aff behind the dishwasher satisfy the accessable part in
422.16(B)(2) and 422.33(A)
The plug has to be "accessible," not "readily accessible." Besides, that is why you need to have a 3-4 foot cord, so there is room to move the DW out of the way, and thereby get to the plug.Wouldn't you need to remove the DW first in order to disconnect it?
The plug has to be "accessible," not "readily accessible." Besides, that is why you need to have a 3-4 foot cord, so there is room to move the DW out of the way, and thereby get to the plug.
I think not. Moving the DW across the floor far enough to get to the plug does not impose an electrical safety hazard. The purpose of the disconnect is to allow you to safely work on the wiring inside the unit.But isn't the purpose of the disconnect so you can safely move the DW out in the first place?
So did I, before I posted my first response. Since I never did actually give you my answer to your question, let me do it now: Yes.That was my first thought, I looked up accessable in art. 100. ????????
I think not. Moving the DW across the floor far enough to get to the plug does not impose an electrical safety hazard. The purpose of the disconnect is to allow you to safely work on the wiring inside the unit.
I agree with Charlie, Yes a receptacle behind a dishwasher would be accessible.
Chris
I think not. Moving the DW across the floor far enough to get to the plug does not impose an electrical safety hazard. The purpose of the disconnect is to allow you to safely work on the wiring inside the unit.
I disagree with both of the moderators above.
Well, I suppose there is a first time for everything.:grin:
The article 100 definition of ?accessible? speaks of moving part of the building, and you don?t have to do that to remove a DW from its place.IMO the disconnecting means for the DW is not accessible located behind said DW.
I consider that to be ammunition in support of my/our point of view. The say that for a range, because they have a reason to think a range is somehow different. My guess would be that ranges are heavier, and tend to get hotter. But they first say that an accessible plug is acceptable as a means of disconnecting an appliance, and then they give credit for the same thing for a range only if there is a drawer. So I conclude it is acceptable for a DW without a drawer.My ammunition that supports this thought is that for a range this is only allowed if removal of the draw allows access to the receptacle. 422.33(B)
Not a single one. But I have installed or replaced a few (in my own home).You have not worked on many DWs have you?
Every time I have installed or replaced one, a single wood screw is all that attached the unit to the counter. There are no live parts anywhere near that screw.In the course of disconnecting it from the counter you may be exposed to live parts underneath the DW.
I agree with that. But the act of sliding the unit away from the wall is not "working on it."IMO you need to be able to kill the power before you have to work on it.
Well, I suppose there is a first time for everything.:grin:
The article 100 definition of ?accessible? speaks of moving part of the building, and you don?t have to do that to remove a DW from its place.I consider that to be ammunition in support of my/our point of view.
The say that for a range, because they have a reason to think a range is somehow different. My guess would be that ranges are heavier, and tend to get hotter. But they first say that an accessible plug is acceptable as a means of disconnecting an appliance, and then they give credit for the same thing for a range only if there is a drawer. So I conclude it is acceptable for a DW without a drawer.
........ The say that for a range, because they have a reason to think a range is somehow different. .........
The plug has to be "accessible," not "readily accessible." Besides, that is why you need to have a 3-4 foot cord, so there is room to move the DW out of the way, and thereby get to the plug.
I think not. Moving the DW across the floor far enough to get to the plug does not impose an electrical safety hazard. The purpose of the disconnect is to allow you to safely work on the wiring inside the unit.
I disagree with both of the moderators above.
IMO the disconnecting means for the DW is not accessible located behind said DW.
My ammunition that supports this thought is that for a range this is only allowed if removal of the draw allows access to the receptacle. 422.33(B)
Bob, 422.16(B)(2)(4) specifically states that a receptacle for a cord and plug connected dishwasher shall be located in the space occupied by the appliance OR adjacent thereto.
Chris
Bob, 422.16(B)(2)(4) specifically states that a receptacle for a cord and plug connected dishwasher shall be located in the space occupied by the appliance OR adjacent thereto.
Chris
I have to wonder if we are envisioning different animals here. I have only dealt with the DW units that go into household kitchens. I can remove one screw just above the door at the front of the unit, and easily slide the unit away from the wall without even opening the door, or touching anything inside or underneath the unit. My hands would be at least 24 inches from the nearest wires, and those are protected by small enclosures. The power cords and the hoses have always been flexible, so there was never a need to disconnect plumbing or electrical wiring, until after the unit was in the middle of the kitchen.This blows my mind coming from you.
I do care. I just don't see an electrical hazard.You are typically a strong supporter of safety for workers and in this case you seem to not care at all about the worker.