..........How long would it take to meg 30 circuits?
2 minutes.
Getting set up to safely megger 30 circuits....... maybe a day.
1-1/2 2hours unless it is an incredibly large house.
29 years ago when we started doing IR, everyone said it was to expensive, not practical and was IR just a gimmick. Today it is pretty much the standard in hospitals and data centers and pretty much accepted industry wide. It was a long slow sale, but the market increased with time.
. Just out of the box the wire had melted at a romax staple and burned about 4 inches up the stud, .
This must happen all the time. I absolutely hate staples and keep my stapling to a minimum. Granted, it's generally operator error but I can't count the number of cables I've seen damaged from overzealous heavy handed staplers.
That's a tiny heating element nailed right into the wood.
You would need to drive that staple not just into the outside jacket but bite into 1 of the wires before it could do what happened here. Staples are not sharp and does not require a lot of skill. I was buying them by the bucket. What happened here is rare. I will assume it was one that did bite in. And do understand that leakage was likely going on for many years. Perhaps all them years with a breaker that can't trip let it get that bad. The new afci might have helped here. They were lucky that the new breaker worked. Have changed out many old panels and never meged any.
And I'd bet you'd have to go through quite a few buckets to get it just right if you were intentionally trying to recreate this incident.
isn't this the reason for arcfault breakers?
yes but now the bigger question, would it have done the job ?