paper romex on an afci

Status
Not open for further replies.

Ravenvalor

Senior Member
Concern

Concern

Jim, just to clarify, what might the concern be?


Larry,

An inspector once told me that an AFCI would not work on old BX cable and Knob and Tube wiring. I did not ask him about the 50's and 60's style paper Romex so I just wanted to get other peoples' opinion before making the recommendation to the customer.

Thanks,
Jim
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Other than indirectly, given that knob-and-tube or the older BX cable will mean it is pretty old and the insulation may not be good enough to allow an AFCI to hold in...
I don't see how poor insulation would affect an AFCI, unless there's severe arcing to ground (sheath, plumbing, etc.)
 

glene77is

Senior Member
Location
Memphis, TN
Larry,
An inspector once told me that an AFCI would not work on old BX cable and Knob and Tube wiring. I did not ask him about the 50's and 60's style paper Romex so I just wanted to get other peoples' opinion before making the recommendation to the customer.
Jim

Maybe not with 40's Romex with the carbon black insulation,
wrapped in paper cord.

I have found enough leakage and induced voltage on 30's K&T so that my Ticker will show 'hot' on the joists, the Neutral, and the Hot.

I have not checked to see if an AFCI would trip over these oldies.

I have very little trouble with 60's Romex with TW insulation.

You will need to set up some sort of test.
And, yes, I need to setup some sort of test, too,
so I'll know for certain what parameters I might be dealing with.
 

glene77is

Senior Member
Location
Memphis, TN
Unfounded, in my opinion. The wiring type has no bearing on AFCI operation.

Unless there is bad insulation and it is leaking, as in small arcing.

I need to setup a test next time I work on one, just to see.
I think my O'scope will show any leaking (arcing) signal.
I don't think the electrical manufacturers have published any standard 'arcing' signal for us to look for. Maybe the whole thing would a possibly complex signal, but I suspect that it will be a hash signal, higher than 1 KHz. But, if it is intermittent, then I may never find it.
I wonder what the digital VOM will show as resistance between conductors. And, the Megger test might be good.

I don't think I got very far with that thought experiment.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I wonder if the lack of a ground with knob and tube will affect the performance of a AFCI?
It sure will. Most of the trips of an AFCI device are from the ground fault protection part of the circuit and not the fancy arc signature detection part.
 