Conductors on messenger.
GKramer
I was wondering what type of conductor/cable one would use to hang on a messenge cable between two buildings. I have a span of about 30' between buildings and I'm not sure if there is industry standard materials for a situation like this. I'm a journeyman electrician new to the fire business.
Thanks
Take a look at Table 396.10(A) for a list of cables that can be installed as messenger supported wiring. (UF cable is on that list)
Chris
I don't think this is approved, but I've got a local AHJ approve this many times for fire alarm circuits underground and aerial:
IMSA cable.
What is it?
It is a cable type most often specified in this area for municipal fire alarm circuits. (The wiring between a building and the fire station.)
IMSA stands for 'International Municipal Signal Association'.
http://www.imsasafety.org/cablespecs.htm
For those that are not used to municipal fire alarm circuits it is pretty much like a 1800s telegraph system. A bunch of transmitters in series with a receiver. Each 'box' taps out the box number and at the fire station they know box 673 is the local Walmart etc.
I kinda think we need to know what the conductors or cable will be used for before we go and offer opinions.
-Hal