Leo, what do you mean by "panel side only"?
Section 250.92(A) requires the bonding of service raceways, cable tray, cablebus framework, auxiliary gutters, or service cable armor and all service enclosures containing service conductors, including meter fittings, boxes, or the like, interposed in the service raceway or armor.
Section 250.92(B) requires electrical continuity of service equipment, but 230.66 does conceded meter sockets as service equipment and bounded by the manufacture.
Since service grounded (neutral conductor) is boded in the meter socket there is not need to bond the nipple between the meter and the service disconnecting means on the meter side.